6/24/2010 9:00 AM
 
[updated:LAST EDITED ON Jun-24-10 AT 07:22 AM (CDT)]We had a leak on the cooling coil made from copper nickel (90/10). I suspect the problem was due to high pH water (almost 10) resulting in dissolution of the material. Is it safe to use titanium or stainless steel cooling coil under these conditions? Are there any other copper family materials, which would be suitable? Thanks a lot
 
New Post
6/25/2010 9:00 AM
 
Dear Kouba31, pl. note that 90-10 Cu-Ni tubes are having excellent general and pitting corrosion resistance under many extreme conditions. This material can withstand very high pH conditions. Before making any conclusion pl. execute one failure investigations with all background operation , mechanical and process data. Pl. also inform the foum the process conditions, failure history and the minimum and maximum velocity of the coil fluids. regards >We had a leak on the cooling coil made from copper nickel >(90/10). I suspect the problem was due to high pH water >(almost 10) resulting in dissolution of the material. Is it >safe to use titanium or stainless steel cooling coil under >these conditions? Are there any other copper family >materials, which would be suitable? Thanks a lot
 
New Post
6/27/2010 9:00 AM
 
Thanks for commenting on the case - this lack of resistance is exactly what puzzles me. It was put in operation in 1996. There were no defects on this component in the past. The water which was used for cooling until 2008 was basically taken from the river without much of the precleaning; on average its pH was 8,5. After 2008 the special clean water was used for cooling until now; on average its pH is 9,8. I do not have information about the flow rate, but I think this not part of the problem, since there are definitely no signs of any erosion on the inner surface of the cooling coil. We did some failure investigation and it appears that the coil defects are linked to these two periods of operation. There were several through-wall dimples on the inner surface, which had blister-like deposits or their remains above them. Chemical microanalysis found sulphur under the deposits. We believe that these defects are caused by MIC, as we had similar problem on the austenitic steel tubing welds where practically the same water flowed. There are areas in the inner surface with more or less surface corrosion were dezinfication is taking place. Corrosion is reaching up to 1/3 of the wall thickness. I think that this may be caused by high pH water used since 2008. The operator claims it detects the defects immediately. Our conclusion is that there was MIC until 2008, but it did not grow through-wall. After 2008 with changed water chemistry the dissolution of the material took place and caused the final fracture. Would this make any sense to you? Thanks for your time. Mark
 
New Post
6/27/2010 9:00 AM
 
(1) Pl. confirm whether your Cu-Ni tubes are C 70600 grade ? (2) Pl. note that good category, like above. Cu-Ni tubes are basically not susceptible to dealloying and SCC (3) It has been established that biofouling is not a major issue for Cu-Ni tubes having more than 80% Copper. Pl. ensure the 1996 year supply TC. (4) What is the color of the encapsulated deposits over the dimples ? From 1996 - 2008 you have used polluted water which will definitely contain lot of air (O2) and sulphides. In aerated water having oxygen + sulphides lead to much higher corrosion current and concurrent corroision rate being localised. Upto 50 g/m3 sulphides and upto 4m/s flow vel corrosion rates are minimal. But above these values corrosion rates are higher. This deposits are stable and cause under deposits corrosion. MIC may or may not contribute too this process. When fresh cooling water ( specially cleaned i.e. deaerated and probably should be clorinated too !! ) these deposits and unstable Cu-S-O2 film will be flushed out and fresh Cu-O film will be form with exposure to all this dimples into cavities leading to thickness redundancy and progressive failures. (5) The issue of sand particles also need to be address. In principle Cu-Ni tubes are proved to perform well in high pH conditions so I feel pH may not be an issue. Only what I feel that all these failure spots has happened as a result of long term use of polluted untreated water. regards >Thanks for commenting on the case - this lack of resistance >is exactly what puzzles me. > >It was put in operation in 1996. There were no defects on >this component in the past. The water which was used for >cooling until 2008 was basically taken from the river >without much of the precleaning; on average its pH was 8,5. >After 2008 the special clean water was used for cooling >until now; on average its pH is 9,8. I do not have >information about the flow rate, but I think this not part >of the problem, since there are definitely no signs of any >erosion on the inner surface of the cooling coil. > >We did some failure investigation and it appears that the >coil defects are linked to these two periods of operation. >There were several through-wall dimples on the inner >surface, which had blister-like deposits or their remains >above them. Chemical microanalysis found sulphur under the >deposits. We believe that these defects are caused by MIC, >as we had similar problem on the austenitic steel tubing >welds where practically the same water flowed. > >There are areas in the inner surface with more or less >surface corrosion were dezinfication is taking place. >Corrosion is reaching up to 1/3 of the wall thickness. I >think that this may be caused by high pH water used since >2008. > >The operator claims it detects the defects immediately. Our >conclusion is that there was MIC until 2008, but it did not >grow through-wall. After 2008 with changed water chemistry >the dissolution of the material took place and caused the >final fracture. > >Would this make any sense to you? Thanks for your time. >Mark
 
New Post
6/28/2010 9:00 AM
 
Mark Kouba 31 Cu Ni alloys are resistant to high pH water and also from reasonable levels of pitting resistance in river water or now changed to high pH de-min water. From description and failure experienced - since the Cu Ni coil had been in service since 1996 it appears the origin of pitting (usually dimples at some places where due to MIC (organic /inorganic) and some conditions of stagnant water during non-use could have initiated the pitting some years back From two years back when you changed the water chemistry from river water, the pre-existing de-zincified or de-nickel areas could have promoted into fine cracks to give this leak in coil Cu Ni is well proven material for sea water (turbid water with high chlorides / sulphides as well) and in high pH water chemistry. For this water chemistry, it is quite suitable and cost effective also. Cu Ni tubes should easily withstand flow rate of 3-4 m/sec for this high pH water chemistry. You had also not seen any erosion problem for the last 15 years (effectively confirming that the flow rate could have been well within design parameters - 3 -4 metres/sec) Considering the 15 year operational success, you might re-think of any material change at this stage unless you had definitely identified the cause as de-zincification or de-nickelification problem combined with MIC and also pitting initiated earlier not diagnozed properly till 2008. For a compounded problem of 15 years,to me it looks, change of material replacement with Ti could be thought of at a later stage after proper failure investigation going through operational and maintenance histories of the cooling coil in 15 years time. Hope this helps C.V.Srinivasan Nishi Engineers Pvt Ltd India June 29, 2010 E-mail; nishi@vsnl.com >Thanks for commenting on the case - this lack of resistance >is exactly what puzzles me. > >It was put in operation in 1996. There were no defects on >this component in the past. The water which was used for >cooling until 2008 was basically taken from the river >without much of the precleaning; on average its pH was 8,5. >After 2008 the special clean water was used for cooling >until now; on average its pH is 9,8. I do not have >information about the flow rate, but I think this not part >of the problem, since there are definitely no signs of any >erosion on the inner surface of the cooling coil. > >We did some failure investigation and it appears that the >coil defects are linked to these two periods of operation. >There were several through-wall dimples on the inner >surface, which had blister-like deposits or their remains >above them. Chemical microanalysis found sulphur under the >deposits. We believe that these defects are caused by MIC, >as we had similar problem on the austenitic steel tubing >welds where practically the same water flowed. > >There are areas in the inner surface with more or less >surface corrosion were dezinfication is taking place. >Corrosion is reaching up to 1/3 of the wall thickness. I >think that this may be caused by high pH water used since >2008. > >The operator claims it detects the defects immediately. Our >conclusion is that there was MIC until 2008, but it did not >grow through-wall. After 2008 with changed water chemistry >the dissolution of the material took place and caused the >final fracture. > >Would this make any sense to you? Thanks for your time. >Mark
 
Previous
 
Next
HomeHomeDiscussionsDiscussionsMaterial Select...Material Select...Copper nickel cooling coilCopper nickel cooling coil


  

News

With a little delay, our Calculation of Ammonium Salt Deposition Temperatures...read more
Our sulfidic corrosion calculators are now available at hghouston.com/calcula...read more

Stay Current

Sign up for our quarterly newsletter

covering updates on corrosion

Sign Up