12/30/2005 9:00 AM
 
Hello all, I am doing failure analysis of hot water heater copper tube. Client noticed some pitting corrosion and subsequent leaks and she replaced that with new 1/2" tube. Now I am doing the analysis to find out why it was leaking. I noticed that it is general corrosion and assume that it may be due to erosion corrosion due to higher velocity associated with temp. I perform chemical test on the the deposit and found no lead and ruled out the corrosion due to flux. Can any one help me to find out the velocity through an 1/2" copper tube when the inlet pressure to the tank is known (55 PSI) and also assume that outlet pressure is same. Ofcourse we know the cross sectional area of the tube. This is a 40 gallon/ hour water heater. Thanks
 
New Post
1/3/2006 9:00 AM
 
At first the cause analysis of Pitting Corrosion has to be calculated i.e. it has suffered from local damages may be due to deposits. But a general corrosion trend can be linked with high flow velocity beyond design and/or due to dual phase flow . However w.r.t. your data after doing necessary calculation pl. try to keep your flow velocity below 1.083 ft/ sec. regards and pl. give your analysis feed back. DM Mobile 94342 36119
 
New Post
1/3/2006 9:00 AM
 
Thanks for the reply. I also think so, that the velocity is the problem. I calculated the velocity for a 40 gallon/ hour water heater is supposed to be 1.08 feet/sec. But when I refered AWWA stanadard (internal corrosion of water distribution system), I learned that erosion corrosion due to high velocity associated with temperature occurs only when the velocity of hot water is above 1.5 feet/sec. That is the reason why I could not argue that. Any insight in to this information. Thanks
 
New Post
1/4/2006 9:00 AM
 
WORLD WIDE SURPLUS; I BUY ALL TYPES OF VALVES,MORE TANKS.MORE.
 
Previous
 
Next
HomeHomeDiscussionsDiscussionsGeneral Corrosi...General Corrosi...Hot water heater copper tube corrosionHot water heater copper tube corrosion


  

News

With a little delay, our Calculation of Ammonium Salt Deposition Temperatures...read more
Our sulfidic corrosion calculators are now available at hghouston.com/calcula...read more

Stay Current

Sign up for our quarterly newsletter

covering updates on corrosion

Sign Up