New Post
11/23/2006 9:00 AM
 
Dear Experts, Our design specification does not require total internal shell wall of gasolene and lighter products tank to be coated. Only the bottom portion is lined (1st course). After 12 years of service, we found out that the middle courses are experiencing corrosion rates higher than anticipated particularly at areas where the floating roof is always located. Our concern with coating is that it might be scrapped off by the weather shield movements. Other light product tanks with floating roof are also showing similar symptoms/conditions. Has anyone experienced this and if so, can you share your mitigation eg. successful coating used? regards, Alani
 
New Post
11/28/2006 9:00 AM
 
Normally corrosion is expected at the middle of the tanks and at vapor space locations.Blasting with High build Epoxy coating(Polyamide or polyamine with one coat of inorganic zinc silicate) will solve the corrosion problem.Check the seal and change the worn-out neoprene sheet.Nowadays with secondary seal the weather shield plate is covered with neoprene sheet for positive vapor sealing and in one way it will avoid metal to metal contact. regards,
 
New Post
12/11/2006 9:00 AM
 
Thanks Krish. I'll check the details of the weather shield design. I think it could be that the neoprene has hardened over the years and was not replaced much earlier.
 
New Post
1/29/2007 9:00 AM
 
This is a known problem in MS or gaoline storage floating roof tanks. The corrosion takes place at the interface of liquid level and atmosphere. The corrosion is maximum with mechanical type pentagon of seals, and less with soft foam seals. The corrosion increases with the number of cycles. Epoxy paintings have been used and have given good results.
 
New Post
2/5/2007 9:00 AM
 
Hi, Our experience is that corrosion is severe in the 3rd-6th shell of an Gasoline or MS tanks. The reason is - the product (gasoline) level is most likely to be in that height for most of the time. The repeated wetting & drying creates ideal condition for preferential corrosion. Our painting requirement for Gasoline / naphtha etc tanks changed after a Failure gasoline tanks in one of our Refineries in 1983. The shell ruptured vertically at 5th shell course. And yes, the secondary seal matters. Sometimes, the mechanical type secondary seal abrades the tank shell repeatedly, and even destroys the paint. We generally go for either HB epoxy paint system or Inorganic Zn Sillicate+HB epoxy paint sytem. And painting is done for full shell internal+bottom paltes. And in some places, even the floating roof internal surface (which is in contact with the product). 'Hope it helps regards
 
Previous
 
Next
HomeHomeDiscussionsDiscussionsOil Refinery Co...Oil Refinery Co...Gasolene Tank Internal Corrosion (floating roof type)Gasolene Tank Internal Corrosion (floating roof type)


  

News

With a little delay, our Calculation of Ammonium Salt Deposition Temperatures...read more
Our sulfidic corrosion calculators are now available at hghouston.com/calcula...read more

Stay Current

Sign up for our quarterly newsletter

covering updates on corrosion

Sign Up